Grounding Electrode System in existing Building (NEC 250.50)

Status
Not open for further replies.

philly

Senior Member
I've been involved in several projects recently where new electrical distribution equipment was being installed in an existing building/structure as part of an upgrade or build out. In most of these cases these do not involve the service entrance to the building but rather are new equipment that are being fed from existing distribution in the facility.

Since most of these installations are indoors (build out of un-used storage space, etc...) most of the time there is not a real practical means of installing grounding electrodes when they are required (As opposed to outdoors just driving a rod, etc...).

The above recent experience has let me to a few questions I was hoping some folks here could shed some light on:

1) With new equipment being installed inside an existing building would the only requirement for having to install a new grounding electrode (or electrode system) be if there was a new separately derived system requiring grounding electrode per 250.30?

2) Are there any specific requirements to ground equipment such as Switchgear, Switchboards, and Panelboards other than the required EGC's or SSBJ's? In other words are there any requirements to bond these to grounding electrode system if not part of SDS as mentioned above? In most outdoor or new civil installations I typically see a bare 4/0 Gnd pigtail tied from the main grounding electrode system (ground grid, ductbank, ground ring, etc...) that the new Switchgear or equipment is tied to. I've always viewed this as best practice as opposed to a requirement?

3) If the grounding of each piece of equipment in #2 above is best practice like I mentioned how is this typically practically achieved in an indoor application where it is not practical to install underground 4/0 ground for bonding equipment to? Is it a practical approach or necessary to install a new ground bar somewhere on the wall in a room/area tied to existing grounding electrode and then run grounds from this ground bar to bond each piece of equipment?

4) In an existing building is there a specific requirement for using existing grounding electrodes per 250.50? What is this existing grounding electrode consists of a ground rod located outside of the building? To me it would not seem practical to try to tie into that existing grounding electrode? Can existing steel columns be used to satisfy the grounding reequipments for SDS or 250.50?
 
You need a GES. If none exists in an old building just pound in two 8' rods minimum 6' apart and you're done.
 
You need a GES. If none exists in an old building just pound in two 8' rods minimum 6' apart and you're done.

I guess I'm looking to understand the requirements as a starting point. I see that 250.50 discusses types and installation of grounding electrode system but not necessarily the requirements for what should be connected to that system. Are there other specific sections that discuss requirements for grounding/bonding equipment to electrode system? In other words is there a specific section that requires a Switchgear lineup to be bonded to GES in addition with the EGC that is run to the switchgear?
 
1) With new equipment being installed inside an existing building would the only requirement for having to install a new grounding electrode (or electrode system) be if there was a new separately derived system requiring grounding electrode per 250.30?
Yes a SDS requires a connection to a grounding electrode system. This often can be structural metal. The GEC connection is made at the same location of the SBJ. You also need to bond any metallic water piping in the area served

2) Are there any specific requirements to ground equipment such as Switchgear, Switchboards, and Panelboards other than the required EGC's or SSBJ's? No, this is a commonly misunderstood practice that serves no useful purpose, The NEC allows ground rods to be installed at say at milling machine and this is called an Auxiliary Electrode, and does not have to meet the requirements for sizing the GEC, depth of ground rod, see 250.54. Keep in mind this type of ground rod serves no useful purpose and often creates more problems than it solves. Some years ago the Electric Power Research Institute did a study on this, found in some cases it helped, some made no difference and often made the problem worse. An isolated ground rods provides an additional path into the equipment in the event of a lighting strike (which is what ground rods are for, not clearing a fault. I sent the information from the study to Mike Holt, and he made a great graphic....

Based on instructing grounding/bonding classes for many years and attending many Mike Holt Bonding and Grounding seminars, what you need to focus on is the low impedance fault clearing path - the green wire. Ground rods don't do much, and there is much misunderstanding on this subject.
You would benefit by getting a copy of Mike Holts Bonding vs Ground book and DVDS.