Hello. I'm hoping to have an informed discussion regarding designs I am evaluating for code compliance and VE opportunities. I consistently see specifications for a 4/0 AWG GEC to all grounding electrodes and other, what I would consider 'overkill', items. One engineer's stance is that "current will travel along the path of least resistance" and that it provides a 'better system.'
Could I please get some eyes on this and confirm my understanding of it all? Thanks in advance for reviewing this wall of text.
#1 - The GES is not intended to clear faults. That is the role of the EGC and bonding conductors. Maximum GEC sizes are based on the physical limitations with 4 AWG (UFER) or 6 AWG (Rods) simply not being able to carry more current than the GE's capable of.
#2 - 4/0 AWG GEC is oversized. Period, always. I've seen it argued that 4/0 would be installed for longevity... I still don't buy it.
#3 - Connections to ground rods need not be larger than 6 AWG, provided that it doesn't extend to any other GEs.
#3A - In fact, we can call it done with just (2) 3/4" x 10' rods spaced 6' apart connected via 6 AWG. This is the most cost effective method.
#4 - There is no added benefit to installing a UFER in addition to any other grounding electrode. Connection is only required if a UFER exists and never needs to be larger than 4 AWG, provided that it doesn't extend to any other GEs.
#5 - A ground ring need not be smaller than 2 AWG and there need only be one connection back to the GES (MBGB). Connecting to 'every other' column offers no added benefit, excluding the situation where it would simply be easier for bonding of various utilities/ services entering at various locations in a larger building.
#6 - Rods are not required at light poles. The EGC is all that's necessary and it does not help in the event of lightning strike.
#7 - Grounding of concrete equipment pads are not code required, assuming all equipment is fed with EGC.
#8 - Triads aren't mentioned in the code nor does it provide any additional benefits to the GES, with the exception if maybe one of the points included an inspection well for ease of maintenance and testing.
#9 - Its fair to assume that modern water pipes will not be metallic and would not be considered a GE? Bonding to interior water piping would still be required. A sprinkler system is not likely to be energized.
#10 - The 'common GEC' is used between the main building ground bar and all other ground bars (ex. riser to connect mbgb to ground bars in sub-electrical rooms in multi-story facility) shall not be smaller than 3/0 AWG. If structural steel is available the riser is not required.
#11 - For static electricity, "the minimum size of the bonding and grounding wire is dictated by mechanical strength not by it current-carrying capacity....A resistance of 1 megaohm or less is generally considered adequate." In short, a 12 AWG bonding conductor to the GES is sufficient for electrostatic discharge, with use of grounding personnel straps.
Could I please get some eyes on this and confirm my understanding of it all? Thanks in advance for reviewing this wall of text.
#1 - The GES is not intended to clear faults. That is the role of the EGC and bonding conductors. Maximum GEC sizes are based on the physical limitations with 4 AWG (UFER) or 6 AWG (Rods) simply not being able to carry more current than the GE's capable of.
#2 - 4/0 AWG GEC is oversized. Period, always. I've seen it argued that 4/0 would be installed for longevity... I still don't buy it.
#3 - Connections to ground rods need not be larger than 6 AWG, provided that it doesn't extend to any other GEs.
#3A - In fact, we can call it done with just (2) 3/4" x 10' rods spaced 6' apart connected via 6 AWG. This is the most cost effective method.
#4 - There is no added benefit to installing a UFER in addition to any other grounding electrode. Connection is only required if a UFER exists and never needs to be larger than 4 AWG, provided that it doesn't extend to any other GEs.
#5 - A ground ring need not be smaller than 2 AWG and there need only be one connection back to the GES (MBGB). Connecting to 'every other' column offers no added benefit, excluding the situation where it would simply be easier for bonding of various utilities/ services entering at various locations in a larger building.
#6 - Rods are not required at light poles. The EGC is all that's necessary and it does not help in the event of lightning strike.
#7 - Grounding of concrete equipment pads are not code required, assuming all equipment is fed with EGC.
#8 - Triads aren't mentioned in the code nor does it provide any additional benefits to the GES, with the exception if maybe one of the points included an inspection well for ease of maintenance and testing.
#9 - Its fair to assume that modern water pipes will not be metallic and would not be considered a GE? Bonding to interior water piping would still be required. A sprinkler system is not likely to be energized.
#10 - The 'common GEC' is used between the main building ground bar and all other ground bars (ex. riser to connect mbgb to ground bars in sub-electrical rooms in multi-story facility) shall not be smaller than 3/0 AWG. If structural steel is available the riser is not required.
#11 - For static electricity, "the minimum size of the bonding and grounding wire is dictated by mechanical strength not by it current-carrying capacity....A resistance of 1 megaohm or less is generally considered adequate." In short, a 12 AWG bonding conductor to the GES is sufficient for electrostatic discharge, with use of grounding personnel straps.