grounding electrode system (ufer)

Status
Not open for further replies.

elecmen

Senior Member
Location
NH
Occupation
Electrician
Hi, I would like to use the rebar encased in the slab that is going to have a manufactured home installed on it as the GES. The slab is 8" thick and the rebar is 1/2" and is over 20'long. It is going to have contact with the earth on the sides. Can this be used per NEC? Thanks any input please.
 
The code language is pretty clear that a permitted/required CEE must include a footing and not just a slab. You are correct that an insulating layer (plastic, tar, or foam, etc.) under a concrete mass disqualifies it as a CEE while insulation on one or both vertical sides does not.

Sent from my XT1585 using Tapatalk
 
What you describe doesn't sound like a footing. Nothing would prohibit bonding rebar in the slab, but it also isn't a qualifying electrode and you must use some other qualifying electrode.
 
Hi, I would like to use the rebar encased in the slab that is going to have a manufactured home installed on it as the GES. The slab is 8" thick and the rebar is 1/2" and is over 20'long. It is going to have contact with the earth on the sides. Can this be used per NEC? Thanks any input please.


The rebar in this case would be an electrode according to 250.52(A)(3).
 
not semantics. it is what the code actually says. they carefully left out allowing the slab to be used as a ufer. I have no idea why, but they were very careful to make it clear a slab did not count.

The code doesn't cover every conceivable scenario - at some point one must evaluate the intent.
 
The code doesn't cover every conceivable scenario - at some point one must evaluate the intent.

in this case it specifically excludes what you are advocating doing.

the first part of the paragraph refers to foundation or footing.

the second part to something being vertical.

the slab is not vertical, not a foundation, and not a footing. therefore it just plain cannot qualify as a CEE.
 
The code doesn't cover every conceivable scenario - at some point one must evaluate the intent.
One potential significant difference is that the slab is in contact with suface soil only, which may be dry and have significantly higher resistivity than the deeper soil around a footing/foundation.
The concept of the UFER ground is that it can be usable even in dry and rocky soil, but the Code tries to provide for the best possible result in every situation.

Sent from my XT1585 using Tapatalk
 
I deal with this in building pump houses.

slab on grade; no ufer, 2 grounding electrodes.

if it has footings, a ufer is required in Washington. Had a customer build a brick pump house to match the main building. Put two ground rods in. Electrical inspector said nope. Have to connect to rebar in footings. Concrete contractor didn’t leave me any exposed rebar to bond to. Had to dig down 18” around entire building and install a continuous loop of bare copper, can’t remember what size. Good thing it was only a 10’x12’ Pump house.

concrete runners for a mobile or modular home are not footings.
 
A concrete slab with a thickened edge is not considered a footing by my AHJ

It might depend on how thick it is. If you required to I have a 24 inch footer and it goes down 24 in it's a legitimate footer. But not all floating slabs have a footer. Some just have like a beam of concrete under the slab.
 
I deal with this in building pump houses.

slab on grade; no ufer, 2 grounding electrodes.

if it has footings, a ufer is required in Washington. Had a customer build a brick pump house to match the main building. Put two ground rods in. Electrical inspector said nope. Have to connect to rebar in footings. Concrete contractor didn’t leave me any exposed rebar to bond to. Had to dig down 18” around entire building and install a continuous loop of bare copper, can’t remember what size. Good thing it was only a 10’x12’ Pump house.

concrete runners for a mobile or modular home are not footings.
If there is no qualifying steel in the footing, then NEC doesn't require you to put one there. Is still optional to put one there though.

Inspectors requiring you to install a ground ring instead aren't exactly right in doing so. If there is qualifying steel in the footing NEC says you must use it as a grounding electrode.
 