donruggs
New member
- Location
- Fredericktown, OH United States
I recently installed a 800 AMP single phase 120/240 volt main service to an office complex. It consisted of 4 meters. 3 were 200 AMP, 1 was 250 AMP with breaker under meter. I paralleled 500 MCM CU into the meter set overhead. I installed a 3/4 x 10' CU ground rod and installed 2Q AWG CU wire to it from the meter set. The rebar in the footer was 1/2" and the cement contractor had run #4 AWG CU and we installed it to the meter set. The plumber installed 1 1/2 CU type K water line to the building which I ran #6 AWG CU wire from the meter set to it. The first electrical inspector passed it and Power Co. supplied power to the meter set. I had a different electrical inspector for rough-in wiring of one office and in our conversation said that I should have installed 2Q AWG not only to the ground rod but also to the water line. The ground rod is 4' away from the meter set and water line is 60'. My argument is that I consider the ground rod as the main grounding electrode and the other 2 as supplemental. I base my argument on the ground rod is less likely to be compromised over the life of the electrical system. Rebar can and will rust, ferrous water lines could be replaced or repaired with plastic thus diminishing grounding integrity. The 2nd inspector said his argument is that the water line and rod are both main grounding electrodes. I know all grounding electrode systems are important and work in concert with each other to insure proper operation of the electrical system. How does the code address this?