hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached sketch I have gas station canopy on top their is cell DC antennas, AC panelboards and equipment. The cell antennas, AC panelboards and equipment are fed from service disconnect on utility pole next to gas station canopy.
The cell antennas enclosure , AC panelboards enclosure and equipment enclosure is bonded to ground bus and ground bus is bonded to canopy steel on top of canopy. Please see attached sketch.
The main service disconnect attached to utility pole has grounding electrode conductor to ground rods. Attached sketch shows that their is bonding jumper from ground rod to ground bus which bonds canopy steel to ground rod.
Questions:
1. Canopy steel if qualified as grounding electrode should be or should not be bonded to as shown on sketch with bonding jumper between ground rods and ground bar/steel?
2. The bonding jumper connecting ground rods and canopy steel does it need to be in conduit or can it be insulated wire not in conduit?
3. Instead of bonding jumper between ground rod and ground bus/steel should their be another grounding electrode conductor connecting from service disconnect to the canopy steel directly?
4. Bonding jumper is connecting ground rods in ground. Can bonding jumper be buried in ground and bonded in the ground as shown on sketch? NEC 2014 say anything about it?
The cell antennas enclosure , AC panelboards enclosure and equipment enclosure is bonded to ground bus and ground bus is bonded to canopy steel on top of canopy. Please see attached sketch.
The main service disconnect attached to utility pole has grounding electrode conductor to ground rods. Attached sketch shows that their is bonding jumper from ground rod to ground bus which bonds canopy steel to ground rod.
Questions:
1. Canopy steel if qualified as grounding electrode should be or should not be bonded to as shown on sketch with bonding jumper between ground rods and ground bar/steel?
2. The bonding jumper connecting ground rods and canopy steel does it need to be in conduit or can it be insulated wire not in conduit?
3. Instead of bonding jumper between ground rod and ground bus/steel should their be another grounding electrode conductor connecting from service disconnect to the canopy steel directly?
4. Bonding jumper is connecting ground rods in ground. Can bonding jumper be buried in ground and bonded in the ground as shown on sketch? NEC 2014 say anything about it?