I have a shed and house in close proximity. So I bonded the grounding electrode systems together. Inspector says this is a code violation when I just thought it was a good idea.
Welcome to the forum.I have a shed and house in close proximity. So I bonded the grounding electrode systems together. Inspector says this is a code violation when I just thought it was a good idea.
He did not cite a code section. He just wanted the ground wire between the house ground rods and she'd ground rods removed?What code section did he cite as a violation? Often the question is when there are two structures within proximity to each other can you use one GES for both so this is a new wrinkle of bonding the two together.
No it is not. I'm well aware of separate structures. Only difference they were so close I bonded house ground rod to shed ground rod which he didn't like.Welcome to the forum.
Is the neutral bonded in the shed? If so, he's correct.
Do you have an explicit NEC citation that would prohibit it, or is it just that it would cause objectionable current?Is the neutral bonded in the shed? If so, he's correct.
It's the old allowance for a 3-wire feeder. Yes, that objectionable current; don't have the code handy.Do you have an explicit NEC citation that would prohibit it, or is it just that it would cause objectionable current?
No argument; we know about that from broken-neutral threads. But, the NEC begins at the service.The latter seems unavoidable whenever two structures both have electrical services but have a common grounded metallic facility (water pipe, cable, etc). So providing a bonding jumper between the GESs would be no worse than that.
How do you define proximity to each other? The NEC gives no distance measurement so if the shed is 5' away do the the separate GES's require bonding together? What about 10', 15' or 20'?He's wrong. You could have even used the same two rods for both structures.
In most instances, all electrodes in close proximity must be bonded together.
As far as I am aware, being installed for separate structures doesn't alter that.
Agree rebonding the neutral at the shed is disallowed when it is supplied by a feeder with EGC from the main structure. For the possibility that "the neutral is bonded at the shed" I jumped to "then the shed has its own service" as that is the only way it would be allowed to have a neutral-ground bond (for a new installation). So my question was actually if the shed did have its own service, whether there would be a prohibition on connecting the GESs.It's the old allowance for a 3-wire feeder. Yes, that objectionable current; don't have the code handy.
If the two structures are close enough that it causes this discussion, they're within proximity.How do you define proximity to each other?
For a 3-wire feeder (no EGC, bonded neutral), they must be isolated, regardless of distance.The NEC gives no distance measurement so if the shed is 5' away do the the separate GES's require bonding together?
Optional, beyond what I said above. I consider it to be a matter of economics and practicability.What about 10', 15' or 20'?
Absolutely agree, and have all along.Since the shed has a 4-wire feeder and a separate EGC I see no code violation by bonding the two GES's together regardless of distance.
Unlike a neutral that is bonded at both ends, in which case, only the earth may "interconnect" them.The two systems were already bonded together inherently through the EGC supplying the shed. I see no harm in theory of having them bonded again through another bonding conductor.
Sorry I should have been clearer about what I meant (or I’m not understanding what you meant, sorry Larry bare with me lol) What I meant and was under the assumption was his shed is fed by a 4wire feeder separated N/G at the shed. With the shed GES connected to the EGC bar in the panel in the shed. Than an additional possible in the dirt bonding conductor connecting both the GES together.Unlike a neutral that is bonded at both ends, in which case, only the earth may "interconnect" them.