Am I reading this right. 250.66 (B) says: You do not have to use a GE Conductor over a #4-if encased in concrete, but you do have to size it per T. 250.66 if not encased?
Am I reading this right. 250.66 (B) says: You do not have to use a GE Conductor over a #4-if encased in concrete, but you do have to size it per T. 250.66 if not encased?
250.66 (B) Connections to Concrete-Encased Electrodes. Where the grounding electrode conductor is connected to a single or multiple concrete-encased electrode(s) as permitted in 250.52(A)(3), that portion of the conductor that is the sole connection to the grounding electrode(s) shall not be required to be larger than 4 AWG copper wire.