W wyboy Senior Member Oct 23, 2014 #1 Can steel water pipe with fusion bonded epoxy coating still be used for a grounding electrode?:rant:
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Oct 23, 2014 #2 wyboy said: Can steel water pipe with fusion bonded epoxy coating still be used for a grounding electrode?:rant: Click to expand... If the metal is not in contact with the ground for 10' or more than it would be a worthless electrode and not compliant. I have no idea if the epoxy is an issue but my guess is that it would insulate the pipe from the earth
wyboy said: Can steel water pipe with fusion bonded epoxy coating still be used for a grounding electrode?:rant: Click to expand... If the metal is not in contact with the ground for 10' or more than it would be a worthless electrode and not compliant. I have no idea if the epoxy is an issue but my guess is that it would insulate the pipe from the earth