5-176 Log #386 NEC-P05 Final Action: Reject
(250.58)
____________________________________________________________
Submitter: Bryan P. Holland, Holland Electric
Recommendation: Add new text as follows:
Where separate services, feeders, or branch circuits supply a building and are
required to be connected to a grounding electrode(s), the same grounding
electrode(s) shall be used and the provisions of (1) are met:
(1) An approved audible or visible alarm shall be installed at each service to
indicate the grounded conductor brought to the service has opened.
Exception No. 1: In industrial installations, with written safety procedures,
where conditions of maintenance and supervision ensure that only qualified
persons service the equipment.
Exception No. 2: Where electric service and electrical maintenance are
provided by the building management and where these are under continuous
building management supervision.
Substantiation: Upon the opening of the grounded (neutral) conductor at one
service, potentially dangerous current will flow between the common
electrodes to both services. Any person who comes in contact with exposed
metal parts at the service equipment or grounding electrode system could be
exposed to lethal current.
Panel Meeting Action: Reject
Panel Statement: The submitter has not provided any technical substantiation
to require monitoring grounding electrode and grounding electrode conductor
integrity by audible and visible alarms. The Code is not structured to protect
against abnormal conditions such as open neutrals that may develop.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15