Hi,
I'd like to post this question again. Looking at table 250.66. Would 3/0 be the largest the grounding electrode conductor would ever need to be using a copper conductor on a parallel sets of service entrance conductors? Example
Eight 500 kcmil per phase. Why?
Thanx
Mark
 
Last edited:
teco said:
Hi,
I'd like to post this question again. Looking at table 250.66. Would 3/0 be the largest the grounding electrode would ever need to be using a copper conductor on a parallel sets of service entrance conductors? Example
Eight 500 kcmil per phase. Why?
Thanx
Mark
Yes, 3/0 copper, or 250 kcmil AL.

edit to add: Thats for the Grounding Electrode Conductor. Not for the Grounding Electrode.
 
Last edited:
For a GEC #3/0 is the largest required. However 250.66 is also used for sizing the main bonding jumper. For conductors larger than those listed in 250.66 a main bonding jumper would be required to be sized at 12.5% of the phase conductors.
 
infinity said:
For a GEC #3/0 is the largest required. However 250.66 is also used for sizing the main bonding jumper. For conductors larger than those listed in 250.66 a main bonding jumper would be required to be sized at 12.5% of the phase conductors.

Thanks very good point.
 