Grounding electrodes and Transformer GEC

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
There's a very large (4 feet diameter), thick wall steel pipe that runs about 50' through a building. The pipe contains air only. They're installing a 3ph, 45kVA delta-wye dry-type transformer/panelboard near the pipe for temporary construction power. There are no available grounding electrodes other than two ground wells that lie about 150' away, outside building.
Construction wants to take the transformer's GEC to the pipe - i.e. bolts/footing. Although the pipe does not qualify as a grounding electrode per 250.52, construction is arguing its not unsafe and will suffice for temp power of about 3 weeks.
Any thoughts?
 
The nec, starting in 250.52, has prescriptive rules on what a GE can be. So your question is easily amswered by those rules, but you also need to review 250.30 ish on SDS.
 
There's a very large (4 feet diameter), thick wall steel pipe that runs about 50' through a building. The pipe contains air only. They're installing a 3ph, 45kVA delta-wye dry-type transformer/panelboard near the pipe for temporary construction power. There are no available grounding electrodes other than two ground wells that lie about 150' away, outside building.
Construction wants to take the transformer's GEC to the pipe - i.e. bolts/footing. Although the pipe does not qualify as a grounding electrode per 250.52, construction is arguing its not unsafe and will suffice for temp power of about 3 weeks.
Any thoughts?
Does the building have a structural steel frame? Take a look at 250.68 (C) (2).
 
Does the building have a structural steel frame? Take a look at 250.68 (C) (2).

The building is very old and hardly any drawings exist. None of the steel appears to be tied to earth electrode defined in 250.52. It sits upon concrete pedestals.


Sent from my iPhone using Tapatalk
 
210 C 2 allows you to use the steel frame as a grounding electrode conductor or as a GEC bonding conductor. So you could potentially use it to get to an existing grounding electrode.
 
210 C 2 allows you to use the steel frame as a grounding electrode conductor or as a GEC bonding conductor. So you could potentially use it to get to an existing grounding electrode.

The structural steel frame unfortunately is not exposed. They’d have to chip thru 2”-3” of concrete -which has an additional sort of ‘floor tile’ finish - in order to reach the steel.


Sent from my iPhone using Tapatalk
 