400A single meter service on a backboard with 2 200A breakers. supplies 2 buildings. Does each of the 2 buildings require grounding electrodes? Ground rods at the service.
One is 70' the other is 200'.
Don't forget the disconnecting means required at each building.
Since there are footings then you are required to use a CEE if they contain 1/2" or larger rebar. It's up to the AHJ to determine how they want to deal with the fact that the CEE wasn't installed.
Ran #4 GEC to rods on exterior so at least I got the wire to the outside