grounding electrodes for separate buildings
benmin
Maine
Master Electrician
400A single meter service on a backboard with 2 200A breakers. supplies 2 buildings. Does each of the 2 buildings require grounding electrodes? Ground rods at the service.
If the AHJ considers them separate structures than yes each will need a grounding electrode system.
How far are the buildings from the backboard?
One is 70' the other is 200'. I was not sure yesterday when I arrived and since they were pouring slabs and both had the panels in the center of the buildings, I drove ground rods and ran CU along with the conduit to the panels. Unfortunately, was unaware of the pouring schedule so was unable to get a UFER ground at the footing
Since there are footings then you are required to use a CEE if they contain 1/2" or larger rebar. It's up to the AHJ to determine how they want to deal with the fact that the CEE wasn't installed.
Don't forget the disconnecting means required at each building.
Main beaker panels
Ran #4 GEC to rods on exterior so at least I got the wire to the outside
I many places that wouldn't be acceptable because use of the CEE is required. If the AHJ accepts your two rods then good for you. :)