Guys,
I normally look to have all ground electrode conductors installed to the first point of disconnect, bond the neutral to ground there, and then use the equipment grounding requirements on in through the system on the load side of the disconnect.
However, I occassionally come across cases where it is very difficult to get electrode conductors such as water pipe and building steel out to an outside main disconnect.
Is there any issue with installing a ground electrode from a ground rod to the outside disconnect, while installing additional ground electrodes such as from water pipe and building steel to the main distribution panel? In this scenario, I believe it would still be best to bond the neutral to ground at the outside disconnect. Do you guys agree and if so, can the service entrance pipe(s) be relied upon as an equipment ground in this case?
Thanks,
Creig
I normally look to have all ground electrode conductors installed to the first point of disconnect, bond the neutral to ground there, and then use the equipment grounding requirements on in through the system on the load side of the disconnect.
However, I occassionally come across cases where it is very difficult to get electrode conductors such as water pipe and building steel out to an outside main disconnect.
Is there any issue with installing a ground electrode from a ground rod to the outside disconnect, while installing additional ground electrodes such as from water pipe and building steel to the main distribution panel? In this scenario, I believe it would still be best to bond the neutral to ground at the outside disconnect. Do you guys agree and if so, can the service entrance pipe(s) be relied upon as an equipment ground in this case?