G goatman59 New member Location bandera tx u.s. Oct 19, 2014 #1 do you need a ground rod on each side of the feeder line equiped with grounding equiptment conductor.:?
do you need a ground rod on each side of the feeder line equiped with grounding equiptment conductor.:?
George Stolz Moderator Staff member Location Windsor, CO NEC: 2017 Occupation Service Manager Oct 19, 2014 #2 In general, no, unless 250.32 comes into play.