Sora Komi
Member
- Location
- Charlotte, N.C.
- Occupation
- Facilities Controls Technician
Hello Everyone -
I have run into a situation that's new to me. We have an air handler that has eight blower motors. These motors are controlled by four drives, two motors per drive. (I have never done this, control more than one motor from a drive, but I know that I need to provide individual short-circuit and motor overload protection for each motor.) The motors have a FLA of 18.2 amps.
So, my main question is about the grounding. The drives are rated at having a continuous input current of 55 amps, and a continuous output current of 44 amps. They have internal factory provided input fuses which are rated at 80 amps. Now, these drives are being fed from a 300 amp circuit breaker that feeds the wires going to a wireway, and taps are going to be made in the wireway for each drive's input.
Normally, if fused individually from a circuit breaker or disconnect, you could use a #10 or #8 ground wire. But Table 250.122 calls for a #4 equipment ground for a 300 amp OCD. Does this mean that I need to make a connection in the wireway and run a #4 ground to each drive? And how is the motor ground wire sized in this type of installation? Thanks for all replies!
I have run into a situation that's new to me. We have an air handler that has eight blower motors. These motors are controlled by four drives, two motors per drive. (I have never done this, control more than one motor from a drive, but I know that I need to provide individual short-circuit and motor overload protection for each motor.) The motors have a FLA of 18.2 amps.
So, my main question is about the grounding. The drives are rated at having a continuous input current of 55 amps, and a continuous output current of 44 amps. They have internal factory provided input fuses which are rated at 80 amps. Now, these drives are being fed from a 300 amp circuit breaker that feeds the wires going to a wireway, and taps are going to be made in the wireway for each drive's input.
Normally, if fused individually from a circuit breaker or disconnect, you could use a #10 or #8 ground wire. But Table 250.122 calls for a #4 equipment ground for a 300 amp OCD. Does this mean that I need to make a connection in the wireway and run a #4 ground to each drive? And how is the motor ground wire sized in this type of installation? Thanks for all replies!