robert8717
Member
- Location
- Seattle Wa
Hello,
My question involves a ungrounded 800 amp disconnect that feeds a boiler. The building that this boiler is in is from the 1930s. I am an inside wireman electrician but usually I am given a drawing about what wire to pull and all the other details. Therefore I would appreciate it if someone could point me to the correct code sections.
I have not gone to visit the site yet. here are the facts I know thus far.
1) 800 amp disconnect does not have a grounding conductor (green wire / bare wire)
2) The conduit that feeds the boiler from the disconnect is run over head in an accessible ceiling
3) This boiler is not original building equipment but nobody can tell me how old it is
4) I believe this is a 480 volt three phase system but I do not know yet for sure
Here are my thoughts about this thus far.
1) I went to table 250.122 and read that this system would require 1/0 grounding conductor
2) Can the grounding( green wire) conductor be on the outside of the conduit?
3) If so, can it be a bare copper wire
4) I do not know if the circuit that feeds this disconnect has a grounding conductor or not
5) At what point is it when the conduit can not count as the equipment ground?
I will update this with more details when I got visit the site, any input would be appreciated
Thank you,
Robert
My question involves a ungrounded 800 amp disconnect that feeds a boiler. The building that this boiler is in is from the 1930s. I am an inside wireman electrician but usually I am given a drawing about what wire to pull and all the other details. Therefore I would appreciate it if someone could point me to the correct code sections.
I have not gone to visit the site yet. here are the facts I know thus far.
1) 800 amp disconnect does not have a grounding conductor (green wire / bare wire)
2) The conduit that feeds the boiler from the disconnect is run over head in an accessible ceiling
3) This boiler is not original building equipment but nobody can tell me how old it is
4) I believe this is a 480 volt three phase system but I do not know yet for sure
Here are my thoughts about this thus far.
1) I went to table 250.122 and read that this system would require 1/0 grounding conductor
2) Can the grounding( green wire) conductor be on the outside of the conduit?
3) If so, can it be a bare copper wire
4) I do not know if the circuit that feeds this disconnect has a grounding conductor or not
5) At what point is it when the conduit can not count as the equipment ground?
I will update this with more details when I got visit the site, any input would be appreciated
Thank you,
Robert