Grounding for an 800 amp disconnect feeding a boiler
robert8717
Seattle Wa
Hello,
My question involves a ungrounded 800 amp disconnect that feeds a boiler. The building that this boiler is in is from the 1930s. I am an inside wireman electrician but usually I am given a drawing about what wire to pull and all the other details. Therefore I would appreciate it if someone could point me to the correct code sections.
I have not gone to visit the site yet. here are the facts I know thus far.
1) 800 amp disconnect does not have a grounding conductor (green wire / bare wire)
2) The conduit that feeds the boiler from the disconnect is run over head in an accessible ceiling
3) This boiler is not original building equipment but nobody can tell me how old it is
4) I believe this is a 480 volt three phase system but I do not know yet for sure
Here are my thoughts about this thus far.
1) I went to table 250.122 and read that this system would require 1/0 grounding conductor
2) Can the grounding( green wire) conductor be on the outside of the conduit?
3) If so, can it be a bare copper wire
4) I do not know if the circuit that feeds this disconnect has a grounding conductor or not
5) At what point is it when the conduit can not count as the equipment ground?
I will update this with more details when I got visit the site, any input would be appreciated
Thank you,
Robert
Hello,
generally not required.
does not matter where the conduit is run
also not relevant
voltage is not relevant either
if you use a wire style EGC
no
a bare wire is a legal EGC but it has to be inside the conduit with the other circuit conductors to be a legal EGC
may or may not matter
metal conduit can be the sole EGC the whole way short of a few special cases such as medical facilities and I think classified areas.
Thank you,
Robert
I don't see an obvious problem here. Metal conduit is a perfectly acceptable EGC.
I do not think I can use the conduit as an egc
If I am reading the code correctly according to 250.118 (2) b. I can not use the conduit as a ground because it is over 20 amp circuit conductors.
Is is that right?
robert
Is is that right?
robert
No you are not reading it right. 250.118 (2), (3), (4) are most likely what applies.
The only way (5) would apply is if you are using flex or sealtite and that is where (a), (b), (c) and (d) are referenced to.