greenawaltmark4
Member
- Location
- US
Good morning all,
I have a 200amp service install on a SFD.
The inspector wanted a disconnect installed after the meter on the exterior because of the length of distance between the meter and panelboard.
Then running 4/0 SER to the panelboard.
My question lies in the grounding connection. I installed 2 ground rods and the water meter jump with 4awg to the panel. I did not bond the panel. Then I bonded the disco. Is this correct or should I have run the EGC to the disco?
Thanks in advance
Sent from my SM-S921U using Tapatalk
I have a 200amp service install on a SFD.
The inspector wanted a disconnect installed after the meter on the exterior because of the length of distance between the meter and panelboard.
Then running 4/0 SER to the panelboard.
My question lies in the grounding connection. I installed 2 ground rods and the water meter jump with 4awg to the panel. I did not bond the panel. Then I bonded the disco. Is this correct or should I have run the EGC to the disco?
Thanks in advance