Curious what you guys think about this.
An 'MV' drive is equipped with only a ground bus and not a neutral bus, which makes sense because it's only powering a motor, thus no line to neutral loads. Consider if you have a delta:wye transformer feeding this load. Naturally, you will have an 'X0' bushing where you could attach a neutral in the future. If you bond the MV drive ground bus (this bus also is grounds the enclosures of the drive and the motor) with the grounding plate at the transformer via a bonding jumper, and also bond your 'X0' bushing to to grounding plate, would you have any reason for concern for circulating currents if line to neutral loads were connected to the transformer secondary at a later date? I'm concerned about equipment grounds carrying current and energizing enclosures unexpectedly. I really appreciate any input you may have. I've attached a sketch for reference.
View attachment MV Drive Grounding.pdf
An 'MV' drive is equipped with only a ground bus and not a neutral bus, which makes sense because it's only powering a motor, thus no line to neutral loads. Consider if you have a delta:wye transformer feeding this load. Naturally, you will have an 'X0' bushing where you could attach a neutral in the future. If you bond the MV drive ground bus (this bus also is grounds the enclosures of the drive and the motor) with the grounding plate at the transformer via a bonding jumper, and also bond your 'X0' bushing to to grounding plate, would you have any reason for concern for circulating currents if line to neutral loads were connected to the transformer secondary at a later date? I'm concerned about equipment grounds carrying current and energizing enclosures unexpectedly. I really appreciate any input you may have. I've attached a sketch for reference.
View attachment MV Drive Grounding.pdf