grounding for meter pack with more than 6 meters

Status
Not open for further replies.

TFish9

Member
Hi, I have a 8 meter, meter pack with a disconnect for them. My question is I have a ground wire from the disconnect enclosure to my 2 ground rods and a ground to my water main. Where does the ground go in the disconnect to the neutral bar? I'm confused cause it failed for not having the gec to the neutral. The way i had it was ground wire from disconnect enclosure to ground rods and ground from mater main to ground bar inside the meter pack not inside the disconnect. where does it get connected to the neutral? There is a seperate lug on the neutral bar inside the disconnect. Thanks
 
Hi, I have a 8 meter, meter pack with a disconnect for them. My question is I have a ground wire from the disconnect enclosure to my 2 ground rods and a ground to my water main. Where does the ground go in the disconnect to the neutral bar? I'm confused cause it failed for not having the gec to the neutral. The way i had it was ground wire from disconnect enclosure to ground rods and ground from mater main to ground bar inside the meter pack not inside the disconnect. where does it get connected to the neutral? There is a seperate lug on the neutral bar inside the disconnect. Thanks

The GEC terminates to the neutral bar.
 
Last edited:
In this case you have two GEC's, one to the rods and the other to the water pipe. They both should terminate in the main disconnect on the neutral.
 