Thank you for your reply..
Doesn't 690.47(c)3 say that i can combine the DC GEC and the AC EGC? as long at it meets 250.166 for sizing?
Yes you can combine those, but that's not what you're talking about doing. You are talking about putting in a
bonding jumper according to 690.47(c)(
2) in the 2011 code. (Your DC GEC is at the array and goes to the two ground rods you mentioned.) The code is less clear on whether you can combine an AC EGC with a bonding jumper, but the 2011 pretty much implies that you can't. 2008 may not imply that in the same way.
I think the intent of the code is to ensure that a bonding jumper run separately from the AC conductors is not used as the EGC. But if you run the bonding jumper with the AC conductors, as you are proposing, then I think it might be okay to combine the functions into one conductor, if terminated properly. Then again, I'm not an EE or a code maker.
As far as 690.47(C)(
3) goes, if you are on the 2011 code and not the 2008 code, the option would be to
remove the ground rods at the array and run your combined GEC/EGC all the way back to the AC distribution equipment. The requirement to have a grounding electrode at the array is only in 2008, it was removed again in 2011. On the other hand, there may be good reasons to keep the rods at the array to help with lightning protection.
It would be helpful to know which code cycle you're required to follow.
so if i am going to run 3/0al for my phases that is the size of the combined conductor?
Again, the bonding jumper requirement is the greater of the AC or DC GEC. The EGC requirement in 250.122 is based on the overcurrent protection rating. I suppose if combined you'd take the largest requirement, but again, I think it's a stretch to assume the code even allows that.
If you're worried about doing it twice, ask your AHJ.