Working on a PV system that has steel I-Beams driven into dirt. Would it be possible to use them for grounding instead of connecting to an EGC?
No. A direct connection to the earth does NOT replace an EGC back to the service.Working on a PV system that has steel I-Beams driven into dirt. Would it be possible to use them for grounding instead of connecting to an EGC?