The Iceman
Senior Member
- Location
- Florida
Article 250.52 (B) (1) Metal underground gas piping sysem is not permitted for grounding. I can understand that you don't want to provide a low impedance path for lightning to a gas pipe. But 250.106 (B) tells use to bond gas pipes in a building or structure that are likely to become energized, and bond it to the service equipment enclosure, grounded conductor at the service, or the GEC. Lightning doesn't just take the path of least resistance, it takes every available path. In doing this don't we provide a path for lightning to the metal gas piping system?