Re: grounding grid calculations
PeterD & Kiloamp7, all primary and secondary distribution systems in the US to my knowledge use a mutli-grounded neutral (MGN), there may be exceptions, and perhaps Charlie can elaborate.
IMO one of the main purpose of the MGN is to carry a portion of neutral load current, as a cost saving measure. You do not have to run a full size conductor. Fairly simple ohm's law if you think about it. What would the impedance of several thousand feet of isolated cable compaired to an paralleled earth return path. The parallel resistance of the MGN is much lower than say an isolated neutral conductor.
There are of course other reasons to MGN such as minimizing voltage drop along the length for safety of utility personnel, lightning protection if ran above phase conductors, etc. Finally earth is used as a fault clearing path @ HV and the MGN aids in this function.
As Bob mentioned there are systems in the US, Utah and Alaska to my knowledge, that uses earth as the only return path called SWER. In that system there is no neutral conductor for a return, only earth. The only purpose of SWER is to eliminate the cost of the neutral conductor all together. SWER is used in remote sparsly populated areas where cost are prohibitive otherwise.