We are constructing a generating facility on a customers site. This facility contains a below grade grounding grid that connects to all of our generators, transformers, electrical enclosures, and to the building structure. The grid is designed to provide effective ground-fault protection and is made of bare copper cable and grounding rods.
Our electrical inspector is requiring, in addition to the grid, that all our phase carrying conduits also contain a grounding conductor. One example where this becomes an issue is our connection between our 480 switchgear and step-up transformer. This connection consists of 8 conduits.
I have always tried to eliminate ground loops to prevent noise in my systems. To have 9 loops created here, I must question this requirement.
Does the grounding grid not satisfy the requirements of Article 250.4 of the NEC 2002? Is there something else I am missing?