beechigby
Member
- Location
- St. Croix US Virgin Islands
I am adding a 2 strings and a 2nd SMA SB3000US inverter to an existing system, in essence a double. the 2nd PV array is next to the first, and the 2nd inverter is next to the first.
the 2 new PV source circuits headed to the Inverter mounted SMA DC Disco (with string fuses and ground fault protection built in) are in a new and separate PVC conduit; the run from array to Disco/inverter is less than 14' on the roof, and 5 ' inside concrete utility room.
the EGC/GEC on the 1st array is #6 and run from the rack + PV panels in the conduit with the PV source circuits down to the 1st inverter Disco and connected to the PE terminal, then out to the utilty service ground rod.
the 2nd array has a #6 wire that runs @5" and connects to the 1st array. there is no green wire in the 2nd conduit with the new PV source circuits. AT the 2nd inverter, I have a #6 going to the final PE terminal in the 1st inverter. Is this correct?
Is it ok to not have a green wire in the 2nd array source circuit conduit (it is a short run)?
would it be better to run the 2nd arrays rack + PV EGC/GEC (could it be #8?) tie to the first array, catch all grd lugs on rails of the 2nd array, then enter the new surce circuit conduit and down to SMA DC disco, and on the existing grd rod?
the 2 new PV source circuits headed to the Inverter mounted SMA DC Disco (with string fuses and ground fault protection built in) are in a new and separate PVC conduit; the run from array to Disco/inverter is less than 14' on the roof, and 5 ' inside concrete utility room.
the EGC/GEC on the 1st array is #6 and run from the rack + PV panels in the conduit with the PV source circuits down to the 1st inverter Disco and connected to the PE terminal, then out to the utilty service ground rod.
the 2nd array has a #6 wire that runs @5" and connects to the 1st array. there is no green wire in the 2nd conduit with the new PV source circuits. AT the 2nd inverter, I have a #6 going to the final PE terminal in the 1st inverter. Is this correct?
Is it ok to not have a green wire in the 2nd array source circuit conduit (it is a short run)?
would it be better to run the 2nd arrays rack + PV EGC/GEC (could it be #8?) tie to the first array, catch all grd lugs on rails of the 2nd array, then enter the new surce circuit conduit and down to SMA DC disco, and on the existing grd rod?