I am just wanna be sure this 2.5MVA transformer primary terminal grounding and bonding is ok - there’s a #4/0 green grounding stubbing up into the chamber from the below ground loop which will be tied to the case on a vendor provided Nema 2-hole pad. The 15kV shields will be also bonded to pad along with the #2/0 EGC routed within the conduit.
We always focus on the secondary side but just wondering if the case should be bonded to the grid or does it even matter?
I am just wanna be sure this 2.5MVA transformer primary terminal grounding and bonding is ok - there’s a #4/0 green grounding stubbing up into the chamber from the below ground loop which will be tied to the case on a vendor provided Nema 2-hole pad. The 15kV shields will be also bonded to pad along with the #2/0 EGC routed within the conduit.