grounding ideas

Status
Not open for further replies.

MBLES

Senior Member
I have a customer who has 2prong recptacles the wiring coming into the
box is 12/2 with ground. the egc was cut off at every recpt not enough to make pig tail to recpt. Any ideas on how to remedy this problem without rewirng whole house. My idea was to raise recpt 6'' to get enough wire for
pigtail in every room.
 

cpal

Senior Member
Location
MA
you may want to read this section. 406.3
(D) (3) Non?Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).
 

MBLES

Senior Member
you may want to read this section. 406.3
(D) (3) Non?Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).

Thanks Charlie
 