081007-0641 EST
440:
You need to analyze your circuit.
Some basics:
Pure water, distilled, is a near perfect insulator. However, it can provide capacitive coupling.
Add some salts, normal tap water, and the water becomes slightly conductive, but very poor compared to copper.
Add lots of salts or acids and conductivity becomes much better, but not like copper.
Build the shower enclosure with copper, a copper floor around the shower, and copper piping. All the copper surfaces and the water coming out of the shower head are at the same potential. Thus, no shock problem within this area and while a person was in this shower the potential of the copper could be raised to 1,000,000 volts relative to earth and still no shock within the shower. You may call this a Faraday shield if you want.
So grounding an electrical system, other than the step potential of getting into this shower, is not the problem.
Thus, you have to analyze where the problem is.
If the shower floor is conductive to one side of the power source, the shower walls are insulators, the water piping is an insulator, the water has normal mineral content, and the water supply is in contact with the other side of the power source, then there can be adequate current flow thru the person taking the shower to cause electrocution.
The step potential problem needs to be considered separately.
So I believe what you need to do is use copper piping for some distance before the shower head and connect this piping to the shower enclosure, floor, and drain. This should make all these items, the showering person, and the water coming into the shower at the same potential. Basically any current flow from the power source thru the water would flow into the copper water pipe and back to the power source thru some path. You want the copper pipe and other shower components to be bonded back to the common of the power source.
My comments are extremes to to set the outer bounds. Fundamentally you want to prevent current flow thru the person in the shower which means zero voltage across the person.
25 ohm, 100 ohm, 1 ohm, and 0.001 ohm ground rods probably have no bearing on the real problem other than step potential.
.