If you have a parallel run of 3 sets of 500 kcmill wires in separate raceways what size grounding/bonding wire is required to be ran?
Need clarification on Art. 250.30 (A)(8)(a) and (b)
Dennis,...
I think you are asking for the egc and that would be based on 250.122 of the OCPD. It must be whatever size that Table dictates and it must be in all 3 conduits.