grounding in patients care

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi,
in a dermatology office, in exam rooms, patients care area ,
how do in terminate the green mc cable with redundant grounding wires in power outlets, receptacles...
Also in host panel, source.????

thank you
 
Most of the guys here wrap the bond wire back around the sheath although that is not required (you can simply clip it).
The insulated equipment ground conductor terminate to the the grounding terminal as required by 250.113 and to the box as required by 250.148.
The redundant grounding does not apply to feeders.
 