Thank you guys for your help on this one... I’ve looked this up and get mixed results so here goes...
I have a 3000’ underground run on a 30amp single pole breaker 277v... I will not bore you with my volt calc but I will be cascading from #2 cu down to #8 cu...
30 amp breaker requires a #10thhn
Can I use #10 thhn from beginning to end of this circuit or must I size the grounding conductor to the current carrying conductor as appropriate as i cascade down to my desired #8?
im sure someone has referenced this in code book before but I’m simply unable to find specific article identifying an answer to my question.. thank you for your patience and help in this...
I have a 3000’ underground run on a 30amp single pole breaker 277v... I will not bore you with my volt calc but I will be cascading from #2 cu down to #8 cu...
30 amp breaker requires a #10thhn
Can I use #10 thhn from beginning to end of this circuit or must I size the grounding conductor to the current carrying conductor as appropriate as i cascade down to my desired #8?
im sure someone has referenced this in code book before but I’m simply unable to find specific article identifying an answer to my question.. thank you for your patience and help in this...