I AM REQUESTING AN INTERPRETATION OF THE 1987 CODE SECTION 250-81,250-83 AND 250-84
CAN THE 250-84 REQUIREMENT "WHEN A SINGLE ELECTRODE CONSISTING OF A ROD , PIPE,OR PLATE WHICH DOES NOT HAVE A RESISTANCE TO GROUND OF 25 OHMS OR LESS SHALL BE AUGMENTED BY ONE ADDITIONAL ELECTRODE"BE MET BY THE ADDITION OF A COLD WATER PIPE MORE THAN TEN FEET AWAY AND MORE THAN TEN FEET IN LENGTH BURIED IN THE EARTH?
FOR YOUR INFORMATION
THE RESISTANCE OF THE ROD IS 280 OHMS,THE COLD WATER PIPE HAS A RESISTANCE OF 192 OHMS,THE ENTIRE SYSTEM HAS A RESISTANCE OF 2.8 OHMS. DOES IT EVEN MATTER WHAT THE RESISTANCE IS AS LONG AS YOU HAVE THE GROUND ROD SUPPLEMENTED BY THE COLD WATER PIPE?
CAN THE 250-84 REQUIREMENT "WHEN A SINGLE ELECTRODE CONSISTING OF A ROD , PIPE,OR PLATE WHICH DOES NOT HAVE A RESISTANCE TO GROUND OF 25 OHMS OR LESS SHALL BE AUGMENTED BY ONE ADDITIONAL ELECTRODE"BE MET BY THE ADDITION OF A COLD WATER PIPE MORE THAN TEN FEET AWAY AND MORE THAN TEN FEET IN LENGTH BURIED IN THE EARTH?
FOR YOUR INFORMATION
THE RESISTANCE OF THE ROD IS 280 OHMS,THE COLD WATER PIPE HAS A RESISTANCE OF 192 OHMS,THE ENTIRE SYSTEM HAS A RESISTANCE OF 2.8 OHMS. DOES IT EVEN MATTER WHAT THE RESISTANCE IS AS LONG AS YOU HAVE THE GROUND ROD SUPPLEMENTED BY THE COLD WATER PIPE?