Almae Member Location General Santos City Feb 16, 2016 #1 Good day! Please tell me what's wrong with this installation?An inspector commented that the grounding cable should be installed and laid through parapet wall and not on the top. Where can I look up to it in the NEC? Attachments grounding.jpg 16.8 KB · Views: 0
Good day! Please tell me what's wrong with this installation?An inspector commented that the grounding cable should be installed and laid through parapet wall and not on the top. Where can I look up to it in the NEC?
Z zbang Senior Member Location Roughly 5346 miles from Earls Court Feb 16, 2016 #2 What does the cable connect to at each end, that matters? Looks kind of like lightning protection; I think that's in NFPA 780 (but didn't check).
What does the cable connect to at each end, that matters? Looks kind of like lightning protection; I think that's in NFPA 780 (but didn't check).
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 17, 2016 #3 That's a pretty common installation method for lightning protection systems in that type of location.
That's a pretty common installation method for lightning protection systems in that type of location.
ron Senior Member Location New York, 40.7514,-73.9925 Feb 17, 2016 #4 You will not find anything in the NEC about that installation type. It looks like lightning protection conductor.
You will not find anything in the NEC about that installation type. It looks like lightning protection conductor.