Grounding Installation

scbunker

Member
Location
Georgia
Occupation
Engineer
Hello all, I have a question. I have a job where my drawings say to install the grounding electrode conductor in Sch 80 PVC to underground. The contractor has installed it per the photos attached, coming out of a hole in the side of the load center then routed down the rack with zip ties.

My question: Is this installation against Code, and what's the code reference? I'm certainly going to write up that it isn't installed per plans. But this doesn't 'feel' per-code and I'd like to provide a code justification.

Thanks for your input!
 

Attachments

  • PXL_20231116_194836466 (Medium).jpg
    PXL_20231116_194836466 (Medium).jpg
    208.4 KB · Views: 21
  • PXL_20231116_194848882 (Medium).jpg
    PXL_20231116_194848882 (Medium).jpg
    222.4 KB · Views: 18

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
In Washington we are not permitted to run GEC exposed per state rule
You show a common method, is it 6 or 4 AWG, 6 requires protection from damage
If the plans that were bid show using Sch 80 that’s the way it should be installed.
Otherwise 2 snips of wire cutters and it’s gone
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Off the top of my head I do not see anything all that awful.

IMO, a violation of the contractual requirements is adequate to red tag it, whether it is code or not.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Also, it’s a violation to attach cables to a conduit, I don’t know if it’s allowed for a GEC
I'm thinking that that conduit is just a support post for the strut and panel. I do agree that it should have been run in PVC down to the ground. I'm also not happy with the way it enters the enclosure- on the side with RTV globed around it. It should at least come out the bottom with the PVC and a male adaptor.

-Hal
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If it's accessible to the public, the Cu will likely be gone soon :)


At an absolute minimum I would require the ty-raps be sunlight resistant
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Also, it’s a violation to attach cables to a conduit, I don’t know if it’s allowed for a GEC
If it contains no wire, it's not conduit, it's just galvanized pipe that resembles conduit.

Yes, it should be installed to both plans and to code, whichever is more restrictive.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Also, it’s a violation to attach cables to a conduit, I don’t know if it’s allowed for a GEC
The code does not actually prohibit it outright. It says something about it being required to be identified for the purpose, a very nebulous term. But given how common such an installation is, I would have to say that it is so identified.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If it's accessible to the public, the Cu will likely be gone soon :)


At an absolute minimum I would require the ty-raps be sunlight resistant
I agree, ugly but code compliant with the correct supports. If it were stapled to a wood post no one would look at it twice.
 

scbunker

Member
Location
Georgia
Occupation
Engineer
Thank you all for your input.
For now, I'm just going to comment that it's not per contract documents.
If asked for further justification, 250.64 says the GEC must be "securely fastened" (which I think I can argue it is not based on how I was able to pull it away from the pipe - if this were stapled to a wooden pole it would hardly budge) and must be installed in conduit where exposed to physical damage. This is at a high school; kids damage what they can. Both of those are subjective, but it's just my opinion, such as it is.
 