I am at a loss here on how to help this customer. Looking to pick some minds to see if anyone has run into this situation before.
A technician was called out to the customers home because of an interruption of service to the customer. Upon investigation, the customer noticed that the cable was melted on the drop side of the ground block. The technician noticed that the ground was to the cold water pipe located in the customers basement about 8 feet away from the ground block. The ground block was located on the outside of the home next to the power meter. The technician replaced the customers service drop and relocated the ground to ground rod approx. 3 feet from the ground block. The technician utilized an amp clamp to check the cable sheath. Upon doing so he recognized that the was getting over 2 amps. The technician notified the customer of the issue and recommended that an electrician come out to investigate the issue. The area power company was also contacted to ensure that the neutral to the home was intact.
The customer contacted their electrician who stated that there was not an issue. The power company also did not find any problems with their feed to the home. Therefore, the customer called us back out there.
Upon the request of the service tech, my supervisor dispatched be out to the home to work with the service tech on finding the issue. Here is what I found:
1) Amperage only appears on the drop side of the ground block (.41A)
2) When the ground is disconnected from the ground block, the meter reads .02
3) The ground was originally run past a ground block to another one. I move reran the ground to a closer ground rod. Both rods are connected together.
4) We had the customer turn on air conditioners inside the home. Upon doing so our readings increased upwards of 1A.
5) The technician and the customer claim that they both have seen readings >4A, I was unable to confirm this.
6) I went to an adjacent customer fed off of the same tap and found that the readings on their cable were at .02.
7) I also made a makeshift ground using some ground wire. I striped the wire approx 4' and stuck it into the ground. I connected it to our ground block and had a reading of .02A on the amp clamp.
I believe that the customer is still having an issue inside their home electrically, as our system is not capable of passing >.5A through the tap. However, with the customer receiving information from their friend electrician, it has been a tough sell.
We decided to leave the ground disconnected from the ground block until the customer was able to get his electrician out tot he home. We were called back out today for the cable again being melted at the side of the home. The customer is going to contact the electrician again so we can all meet out there at one time. I would like to be prepared with some knowledge before hand.
Any help is greatly appreciated.
A technician was called out to the customers home because of an interruption of service to the customer. Upon investigation, the customer noticed that the cable was melted on the drop side of the ground block. The technician noticed that the ground was to the cold water pipe located in the customers basement about 8 feet away from the ground block. The ground block was located on the outside of the home next to the power meter. The technician replaced the customers service drop and relocated the ground to ground rod approx. 3 feet from the ground block. The technician utilized an amp clamp to check the cable sheath. Upon doing so he recognized that the was getting over 2 amps. The technician notified the customer of the issue and recommended that an electrician come out to investigate the issue. The area power company was also contacted to ensure that the neutral to the home was intact.
The customer contacted their electrician who stated that there was not an issue. The power company also did not find any problems with their feed to the home. Therefore, the customer called us back out there.
Upon the request of the service tech, my supervisor dispatched be out to the home to work with the service tech on finding the issue. Here is what I found:
1) Amperage only appears on the drop side of the ground block (.41A)
2) When the ground is disconnected from the ground block, the meter reads .02
3) The ground was originally run past a ground block to another one. I move reran the ground to a closer ground rod. Both rods are connected together.
4) We had the customer turn on air conditioners inside the home. Upon doing so our readings increased upwards of 1A.
5) The technician and the customer claim that they both have seen readings >4A, I was unable to confirm this.
6) I went to an adjacent customer fed off of the same tap and found that the readings on their cable were at .02.
7) I also made a makeshift ground using some ground wire. I striped the wire approx 4' and stuck it into the ground. I connected it to our ground block and had a reading of .02A on the amp clamp.
I believe that the customer is still having an issue inside their home electrically, as our system is not capable of passing >.5A through the tap. However, with the customer receiving information from their friend electrician, it has been a tough sell.
We decided to leave the ground disconnected from the ground block until the customer was able to get his electrician out tot he home. We were called back out today for the cable again being melted at the side of the home. The customer is going to contact the electrician again so we can all meet out there at one time. I would like to be prepared with some knowledge before hand.
Any help is greatly appreciated.