Originally posted by dereckbc:
Victor the short answer is yes. If the cabinets have any type of electrical circuits such as power or signal in or around them, you are required to ground the cabinets. It doesn't matter if they qualify for 645 or not. If the racks/cabinets have AC installed in them and the EGC is bonded by some means then you have met the minimum requirements of the NEC.
If the racks are supplied by 48 volt DC power then a DC frame ground will be needed. The DC frame ground is similar to an EGC, except it is not run with battery conductors, and is larger than required by NEC 250.122.
However neither of these two grounds will meet the requirements of equipment manufactures signal ground requirements. This type of ground is typically constructed via # 4 AWG grid under the raised floor system, then each cabinet/rack is bonded to the grid in addition to any EGC supplied via AC power. This is an engineering design question not an NEC issue.