Hey guy first time poster .I live in mass.I am installing a jacuzzi and all the plmbing is pex ,do I have to run my number 8 all the way to the basement
Yep, but with a lot less chlorine!No, you are not ever required to run the 8 AWG bonding conductor back to the panel.
But there a lot of other requirements, if the hot tub is outside you must treat it like a pool.
Is it a hydro-massage tub or a hot tub. To me a Jacuzzi is a hydro-massage tub used in a bathroom.
I agree, when I hear the term "jacuzzi" I envision a hydro massage bathtub.
The answer really depends on what the OPer is calling a "jacuzzi".
Why does it matter.
A hydro-massage tub has much different rules than a hot tub which is treated like a pool.
Its a hydro massage tub in a bathroom ,I meant run it to the basement where I cold find copper pipes because of the pex in the bath
680.74 Bonding.
All metal piping systems and all grounded metal parts in contact with the circulating water shall be bonded together using a solid copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG. The bonding jumper shall be connected to the terminal on the circulating pump motor that is intended for this purpose. The bonding jumper shall not be required to be connected to a double insulated circulating pump motor. The 8 AWG or larger solid copper bonding jumper shall be required for equipotential bonding in the area of the hydromassage bathtub and shall not be required to be extended or attached to any remote panelboard, service equipment, or any electrode.
Sorry its a hydro massage tub ,force of habbit.Like I said the plumbers ran pex to the bath ,so the only actual copper piping is in the basement.Not to sure if I can run # 8 solid down two floors to the basement ,where i can get copper
If the motor has a grd. lug on it. You ground it to the bath tub faucett (spicket) The small piece of metal right before it attaches to pex.
Sorry its a hydro massage tub ,force of habbit.Like I said the plumbers ran pex to the bath ,so the only actual copper piping is in the basement.Not to sure if I can run # 8 solid down two floors to the basement ,where i can get copper
Why would you suggest this?
In the installation described by the op NO bonding is required.
It's part of the circulating system. Our AHJ's make us do it. Only if the motor has a grd lug on it.
It's part of the circulating system. Our AHJ's make us do it. Only if the motor has a grd lug on it.