Have a client that wants to add a large temporary tent in their parking lot due to COVID, fed from the main building service with a 200A 4W feeder.
Art 525 seems to treat the temporary tents as being fed directly with a utility service. Seems to me that I could specify a 4W+G feeder to a disconnect at the tent and provide grounding electrodes at the tent but not bond the neutral to ground. Sound right? Thanks