I've read a lot of posts about bonding in the transformer but mostly about whether grounding bushings are required or not. Our local inspector is asking for a grounding locknut on the flexible conduit coming into the secondary side of the transformer.
To give more detail, we have a transformer being fed from a breaker in a large panelboard. Transformer drops the voltage and the secondary out feeds another panelboard. EMT conduit being used on the primary and flexible metal conduit on the secondary with listed fittings (standard locknuts/lockrings). We punch our own holes for these, no concentric. Everything bonded to XO in the transformer including an EGC to primary and secondary panels, GEC, bonding jumper and frame bond. Basically wired up with the steps outlined by Mike Holt and EC&M.
Is a grounding locknut required on the secondary conduit connection in the transformer? If so, where can I find it referenced in the NEC? If not, what can I use to defend my position?
Thanks.
To give more detail, we have a transformer being fed from a breaker in a large panelboard. Transformer drops the voltage and the secondary out feeds another panelboard. EMT conduit being used on the primary and flexible metal conduit on the secondary with listed fittings (standard locknuts/lockrings). We punch our own holes for these, no concentric. Everything bonded to XO in the transformer including an EGC to primary and secondary panels, GEC, bonding jumper and frame bond. Basically wired up with the steps outlined by Mike Holt and EC&M.
Is a grounding locknut required on the secondary conduit connection in the transformer? If so, where can I find it referenced in the NEC? If not, what can I use to defend my position?
Thanks.