Tom.Margillo
Member
Why is it necessary to put a ground loop around a building or structure. 4/0 bare copper around a building with ground rods every 20' then off of every other steel column a 4/0 cad-welded tieing into the loop.

Cellular towers and aircraft hangers have this type of protection. Look at NFPA #780.Originally posted by Tom.Margillo:
Why is it necessary to put a ground loop around a building or structure. 4/0 bare copper around a building with ground rods every 20' then off of every other steel column a 4/0 cad-welded tieing into the loop.![]()
![]()
That was design issue. By code they have to be bonded at some point.Originally posted by Tom.Margillo:
When I installed Lightning Protection on the same building that had the ground loop,ring,halo it was not permitted to attach to the same loop, a new loop had to be installed the same way the ground loop was. Talk about overkill.
That is cetainly one way of doing it. Most of my designs that use a ring and have LPS I will take the down conductor to a rod loacted just outside the ring. The rod then will be bonded to the ring and have a radial extended outward from the building. For Towers the will be a ring around the tower and building bonded to together with a ground grid mat made of # 6AWG. On the corners of the building and each tower leg there are radials extending outward.Originally posted by physis:
Isn't something like a ring used, with radial wire electrodes extending from the ring outward, for protection of structures that are very susceptable to lightning?
No and if did not quite likely to burn down the building or kill someone. That is why it is required to be bonded.Originally posted by Tom.Margillo:
Wouldn't there be a risk of sending the lightning back into the building when you bond them together.
Now this is an miss-application. Military facilities that use zone RED areas to house sensitive communications will embed a copper screen (not unlike the window screen on your windows)in the walls and ceiling to form a EMI shield to prevent RF leakage and detection. They shield is then bonded to the ring and all other electrodes.Originally posted by haskindm:
I installed a ring like this and air terminals on a building. The building owner told me that they were requiring it, not for lightning, but for security.
What 250.60 says is that you can't use the air terminal conductors and their associated electrodes in lieu of the grounding electrodes that the electrical system requires. You need to satisfy the rules in 250.50 (for creation of a grounding electrode system), separately from what you do with lightning protection.Originally posted by Tom.Margillo:Talk about overkill.
250.60 says that it does not prohibit you from bonding the building's GES to the lightning protection system's electrodes. What I do not know is what, if anything, requires it. I know that 800, 810, and 820 have rules about bonding the electrodes associated with communication systems to the building GES. What requires the same for the lightning protection system?Originally posted by dereckbc: By code they have to be bonded at some point.
250.50Originally posted by charlie b:
250.60 says that it does not prohibit you from bonding the building's GES to the lightning protection system's electrodes. What I do not know is what, if anything, requires it.
I can not understand your position.Originally posted by charlie b:
So I don't think 250.50 gets us there.