Hi,
A question came up that the local AHJ doesn't want the main building transformer and the 4W 480V switchgear it feeds grounded to the same grounding electrode system (ground ring plus several ground rods). Both pieces of gear are located about 15' apart so can easily run to the same grounding electrode system. To be clear, they have separate grounding electrode conductors, just share the electrode system. I can't exactly follow his rationale so wanted to see if others have run into this.
While it is not conventional to connect the two grounds together, I don't see any issues that would be caused by this. There is a safe path for any fault current from any downstream equipment back to the source/transformer.
A question came up that the local AHJ doesn't want the main building transformer and the 4W 480V switchgear it feeds grounded to the same grounding electrode system (ground ring plus several ground rods). Both pieces of gear are located about 15' apart so can easily run to the same grounding electrode system. To be clear, they have separate grounding electrode conductors, just share the electrode system. I can't exactly follow his rationale so wanted to see if others have run into this.
While it is not conventional to connect the two grounds together, I don't see any issues that would be caused by this. There is a safe path for any fault current from any downstream equipment back to the source/transformer.