Mustwin351
Senior Member
- Location
- Texas
I have a manufactured building I am running a 4 wire circuit from 1 of 2 outdoor 200A subpanels (not a service) that sit next to each other. The subpanels have 1 ground rod driven next to them and the panels are about 12-15 feet away from the manufactured building. In this case do I need a separate ground rod for manufactured home's inside panel or does my equipment grounding conductor with my circuit satisfy my grounding requirements?
Also, 3 washers and 3 dryers will be added to this manufactured building. It's panel will not support the additional load...Any problems with running circuits from the second outdoor panel (remember there are two 200A panels) for the washers and dryers? Of course all conductors would be sized appropriately taking into account conductor derating, amacity...etc...with an equipment grounding conductor sized correctly.
I found similar discussions in the forum but not specific to my question.
Also, 3 washers and 3 dryers will be added to this manufactured building. It's panel will not support the additional load...Any problems with running circuits from the second outdoor panel (remember there are two 200A panels) for the washers and dryers? Of course all conductors would be sized appropriately taking into account conductor derating, amacity...etc...with an equipment grounding conductor sized correctly.
I found similar discussions in the forum but not specific to my question.