Grounding Metal Wireways

Status
Not open for further replies.

shortcircuit2

Senior Member
Location
South of Bawstin
Why is there no guidance for grounding Metal Wireways in article 376? Am I required to ground the Wireway if fed by nonmetallic raceways with wires passing through without splice? Looking for code references please...
 
If the egc is a wire type since the conduit in your case doesnt qualify. That in itself may force the issue of bonding the enclosure.

Sent from my LGLS770 using Tapatalk
 
Good idea IMO. Submit a proposal for the 2017 NEC.
Way too late for a PI (public input, previously knows as a proposal) for the 2017 NEC.

The "first draft" (previously known as the ROP) for the 2017 NEC is out for public comment now.
 