For Ethernet communications cables (Cat5 or 6) installed in rigid steel conduit is the conduit required to be grounded?
For Ethernet communications cables (Cat5 or 6) installed in rigid steel conduit is the conduit required to be grounded?
And a counterpoint in that argument may well be 250.86 Exception No. 2.... Many might argue that 250.104(B) applies here. ...
I think you may mean bonded. Many might argue that 250.104(B) applies here. IMO it is a good practice to bond all metallic systems.
I have never liked that phrase. There should never be any non-current-carrying metal parts "likely" to become energized. Making those parts very unlikely to become energized is a major premise of the NEC. I see it as a contradiction of terms.It would depend on whether the exposed metal is considered likely to become energized.