peter d Senior Member Location New England Feb 27, 2009 #21 stickboy1375 said: You ain't kiddin'! Click to expand... Someone needs to explain to NU that it's not the end of the world to have the GEC land in the meter socket. :roll:
stickboy1375 said: You ain't kiddin'! Click to expand... Someone needs to explain to NU that it's not the end of the world to have the GEC land in the meter socket. :roll:
glene77is Senior Member Location Memphis, TN Feb 28, 2009 #22 stickboy1375 said: Look at the picture I posted. Click to expand... If the image "Token" has expired, then open in a New Browser. Also, if the Meter is a Service Disconnect, would that make the Load Center Main OCPD become the 'Last' Service Disconnect? Comments? Last edited: Feb 28, 2009
stickboy1375 said: Look at the picture I posted. Click to expand... If the image "Token" has expired, then open in a New Browser. Also, if the Meter is a Service Disconnect, would that make the Load Center Main OCPD become the 'Last' Service Disconnect? Comments?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 28, 2009 #23 glene77is said: Also, if the Meter is a Service Disconnect, Comments? Click to expand... just a meter socket and not a combo ? not service equipmet ! NEC 230.66
glene77is said: Also, if the Meter is a Service Disconnect, Comments? Click to expand... just a meter socket and not a combo ? not service equipmet ! NEC 230.66