Grounding meter enclosures

Status
Not open for further replies.
Re: Grounding meter enclosures

There is a 200 amp single phase meter underground fee, underground load near where I live that was recently installed to serve a cellular tower about 150 feet away. It does not seem to have a local ground rod and it most certainly does not have a service switch. I do know that Parma, Ohio requires PVC or gavanized rigid conduit for underground services in new construction and permits service cable for replacement overhead services.

However, sooner or later the meter manufacturers are going to require an effective lightning ground for meter sockets. Most lightning damage comes from very small lightning strikes. I was told by a cable plant technician for Ohio Bell ( now SBC ) that 97% of lightning damage in a telephone cable plant comes from silent lightning and invisible lighting. This was after grandmother's phone died during a rain storm during which we heard no lightning. Then he told me that when one you can see and hear strikes, there are about 100 side strikes over a 100 yard radius.
 
Re: Grounding meter enclosures

FYI, all of the meter fittings I have seen have a gap type lightning arrester built into them and dissipates the stroke to the grounded conductor where it will have a path to earth. The fitting and meter are both inexpensive so we do not care if they are destroyed with lightning. We also permit a GEC to be installed from our meter fitting. Policies for other electric utilities are different. :D
 
Re: Grounding meter enclosures

Thanks guys! As an electrician (10 yrs) turned poco design engineer (<2 yrs) in a small rural community, I have seen this issue pop up from time to time. Great to hear the varity of responses.
 
Re: Grounding meter enclosures

In the area that I work in here in Colorado. One of the power companies install a 2-in one meter enclosure a meter with a breaker which may or may not be service equipment ratedor listed. This power company owns, supplies & installs it on the pole & it is the responibilty of the home owner/electrical contractor to go from the bottom side of that enclosure. In the other area that I work in they just now started installing the meter enclosure on the pole but if it is an under ground service to the house it is required by the power company that we install a disconnecting means below the meter.which when we do this than it is required that we ground & bond that disconnect.
 