A couple questions about GEC for a meter housing feeding a main breaker indoor panel with no outdoor disconnect. I know one proper way to ground would be to run ground from the indoor panel to the cold water and also to a ground rod.
Question, I have seen some meter housings connected to a ground rod, but then where is the second GEC and what do you do with the neutral bar and grounding bar at indoor panel? I found this info I'll include below but this is for a disconnect outside I'm wondering for when there is no disconnect outside. Thanks
A. Either location is fine with the NEC. The rule states that the grounding electrode conductor must connect the service neutral conductor to the grounding electrode at any accessible location, from the load end of the service drop or service lateral up to and including the service disconnecting means [250.24(A)(1)].
Question, I have seen some meter housings connected to a ground rod, but then where is the second GEC and what do you do with the neutral bar and grounding bar at indoor panel? I found this info I'll include below but this is for a disconnect outside I'm wondering for when there is no disconnect outside. Thanks
![3-19-09CodeQ&Aweb.jpg](http://ecmweb.com/nec/code_qa/3-19-09CodeQ&Aweb.jpg)
A. Either location is fine with the NEC. The rule states that the grounding electrode conductor must connect the service neutral conductor to the grounding electrode at any accessible location, from the load end of the service drop or service lateral up to and including the service disconnecting means [250.24(A)(1)].