I have read the following exception in the NEC:
 
250.142 Use of Grounded Circuit Conductor for Grounding Equipment.
(B) Load-Side Equipment.
Exception No. 2: It shall be permissible to ground meter enclosures by connection to the grounded circuit conductor on the load side of the service disconnect if
(a) No service ground-fault protection is installed, and
(b) All meter enclosures are located near the service disconnecting means, and ...
 
Question: Can you explain the REASON of the (a) and (b) conditions?
 
Thanks.
 
Ruben
	
		
			
		
		
	
				