Dear Mr. Holt,
Would you please help me with the following questions:
1) A 200HP motor starter is mounted on 13.8KV, 50MVA, 3000A generator skid.
There are 2 ground wires on this motor, one is connected to the base of
generator skid (the generator skid is connected to the ground grid), the
other (equipment ground) is connected to the motor control center located in
the Control house. Could you please let me know how to size the ground
conductor that connected to the generator skid, and the equipment ground
conductor that connected to the motor control center. Does NEC require to
have the ground conductor that connected to generator skid in addition with
the equipment ground conductor? If yes, what is the function and what do we
call this ground conductor?
2) CSA inspector required us to ground all 24VDC pressure transmitters
located on the gen. skid, all the metallic armor cables that connect to
these transmitters also being grounded. What size of ground conductor should
we use to ground the 24VDC instrumentation and what is the purpose of
grounding these 24VDC sensors?
3) My existing ranger draw about 23A and has 10AWG conductor & 30A breaker,
is it OK if I replace it by a ranger that draws only 15A without changing
the breaker?
Would you please help me with the following questions:
1) A 200HP motor starter is mounted on 13.8KV, 50MVA, 3000A generator skid.
There are 2 ground wires on this motor, one is connected to the base of
generator skid (the generator skid is connected to the ground grid), the
other (equipment ground) is connected to the motor control center located in
the Control house. Could you please let me know how to size the ground
conductor that connected to the generator skid, and the equipment ground
conductor that connected to the motor control center. Does NEC require to
have the ground conductor that connected to generator skid in addition with
the equipment ground conductor? If yes, what is the function and what do we
call this ground conductor?
2) CSA inspector required us to ground all 24VDC pressure transmitters
located on the gen. skid, all the metallic armor cables that connect to
these transmitters also being grounded. What size of ground conductor should
we use to ground the 24VDC instrumentation and what is the purpose of
grounding these 24VDC sensors?
3) My existing ranger draw about 23A and has 10AWG conductor & 30A breaker,
is it OK if I replace it by a ranger that draws only 15A without changing
the breaker?