eddycurrents
Member
Hello all. I had some questions to ask about a service I installed on a 12 unit apartment complex. I installed 2 - 6 gang meter bases, with built in disconnects, to feed power to each apt. I have two service risers that the poco will connect 1 service drop to. When it came time to ground the 2 meter bases I followed 250.64(D). Each service riser had a 350 kcmil ungrounded conductor so I ran a 2/0 copper wire to the cold water ground. (350 + 350 = 700 kcmil, table 250.66). I landed the 2/0 to 1 meter base and dropped out of the 2nd with a #2 which I used a split bolt to connect to the cold water grounding electrode. There is a picture on page 201 of the NEC handbook that shows exactlly what I did. Plus the Soares Book on Grounding says I can use a split bolt for my connection on page 103. I then drove 1 ground rod which I ran a #6 from this and used a split bolt to connect it to the 2/0 cold water ground. Was this the correct way to ground these two meter bases? The inspector turned it down. He said that (1)you can NEVER use a split bolt on any grounding electrode conductor, tap or not. (2) I needed to treat each meter pak as its own service (3) I need to run a seperate cold water ground for each service, and (4) I need to drive a seperate ground rod for each meter pak. Does any of this sound correct? Thanks for any replies.